Unable to view rooms with Screenmate

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to view rooms with Screenmate
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1350 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to view rooms with Screenmate

Picard Product_Support
‎2018-09-10 11:13 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:07 PM

Issue

Unable to view rooms with Screenmate. After logging in and typing a room number, Screenmate takes a long time searching for the room and eventually times out.

Product Line

TAC Vista

Environment

  • TAC Vista 5.1.X
  • Screenmate 5.1.X

Cause

This may be caused by slow network communication if Vista is running on a number of networks on a node. Vista will check all nodes for the given Screenmate ID and this can take a long time if there are a lot of objects and/or nodes.

Resolution

To resolve this issue it is possible to activate a caching function that collects the names of all the available Screenmate objects on all the nodes and stores them in a cache file. This means that the next time a user tries to view a room Screenmate will check in the cached file instead of asking all nodes for their Screenmate objects. To activate this function do the following:

  1. Locate the web.config file for TAC Vista web
    1. By default this is in c:\inetpub\wwwroot\TACVistaWeb51X\
  2. Open the file (with notepad) and locate the key TAC.WebStation.ScreenMate.CacheEnabled
    1. Change the value of this key to "True" and save the changes to the file.
  3. Create the cache file
    1. Open a web browser and type in Localhost/ScreenMate
    2. Try to browse to a room once logged into Screenmate. This will create the cache file.
    3. Check under C:\Windows\Temp and see that a file named ScreenMateCache.dat has been created.
  4. If the file isn't created:
    1. Temporarily delete the other Vista nodes in Vista workstation so that only the master is left.
    2. Rerun the steps above  - this will create a file containing the local screenmate objects and speed the process up.
    3. Add the other TAC Vista nodes again and repeat the steps above shown under "Create the Cache File".

The next time the process should be much quicker, once this file is created.

If problems persist check the authority settings described in The ScreenMateCache.dat file is not created on a Windows 2008 server.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7643
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore