Event notification is grayed out in the AS and will not allow configuration.
Cannot add a category within the AS.
  • SmartStruxure
  • Shadow
  • AS
  • Event Notification
The Event Notification in the AS can be locked due to a shadow relationship with an Event Notification in the ES.
  1. Note the IP address of the AS, as the shadow relationship can be re-established after necessary changes are made.
  2. Remove the shadow relationship to the ES to allow configuration of the AS. Detailed instructions can be found in Unable to add an Automation Server underneath an Enterprise Server.
  3. Re-established the shadow relationship if needed.