Unable to send alarm generated emails via the Yahoo SMTP server in I/A Series G3.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to send alarm generated emails via the Yahoo SMTP server in I/A Series G3.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3349 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to send alarm generated emails via the Yahoo SMTP server in I/A Series G3.

Picard Product_Support
‎2018-09-11 02:18 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:21 AM

Issue

Unable to send alarm generated emails via the Yahoo’s SMTP server in I/A Series G3. The following error messages are displayed in the console output window when attempting to send a mail via Yahoo’s SMTP server.

  • javax.mail.MessagingException: Could not connect to SMTP host: smtp.mail.yahoo.com, port: 465;
  • Caused by: java.net.ConnectException: Connection refused: connect

Product Line

TAC I/A Series

Environment

  • Niagara G3
  • ENS
  • ENC-520
  • ENC-410

Cause

An incorrect STMP hostname was used in the “Hostname” of the OutgoingAccount. The correct Yahoo outgoing mail address, “smtp.mail.yahoo.com”, must be entered for in the OutgoingAccount “Hostname”.

Resolution

Procedure and properties settings required when using the Yahoo SMTP Server:

  1. Add the EmailService and CryptoService to the station's Services folder. If emails are to be sent from an ENC, ensure that the email and crypto modules (and their dependencies) are installed into the ENC.
  2. Add the OutgoingAccount to the EmailService.
  3. In the OutgoingAccount properties, configure the properties indicated below. Leave other properties as their default settings.
    • Hostname: smtp.mail.yahoo.com
    • Port: 465 (this is the TCP port SMTP over SSL uses)
    • Account: example@yahoo.com (works without the “@yahoo.com” as well)
    • Password: Your Yahoo account password
    • Enabled: true
    • Use SSL: true (Yahoo requires SSL)
    • Transport: Smtp
    • Use Authentication: true (Yahoo requires authentication when sending out emails)
    • Reply to: example@yahoo.com (“The Reply To” must contain a valid Yahoo account)
  4. You can test the functionality by right-clicking on the EmailService and selecting 'Actions' > 'Send' to send out an email.

Notes:

  1. CryptoService enables the SSL feature in the G3 station.
  2. The crypto module is included in the installation of I/A Series G3 version 3.6 but it was not included in earlier versions. You can download the crypto modules for earlier versions of G3 from The Exchange Download Center.
  3. Ensure that the station is licensed for crypto. You can look into your license file to check. Below is an example taken from a demo license.
    feature expiration="2012-03-31" name="crypto" parts="ENS-DEMO" ssl="true"
Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 12976
  • RyanSuar19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore