Unable to reset b3 flash circuit breaker to continue backing up to flash.
  • Unable to reset b3 flash circuit breaker to continue backing up to flash.
  • RobertAndriolo
    RobertAndriolo
  • AdamSteele
    AdamSteele
  • Dave_Shore
    Dave_Shore
‎2018-09-06 08:35 AM
Last Updated: Guinan RobertAndriolo Guinan ‎2019-06-18 08:37 PM
StatusBackup "State" system variable is not able to be manually changed and attempting to set this variable to Enabled produces a script error instead of resetting the flash circuit breaker.
  • Building Operation v1.8 and below.
  • b3/i2 Controllers
Feature to reset flash circuit breaker was not implemented in the earlier versions of Building Operation
A new feature to reset the flash circuit breaker was implemented in Building Operation v1.9 to address this issue. The b3 BACnet Device Memory on-line help topic shows how this is manually reset from the WorkStation in the Device menu.