Unable to connect to a controller with a laptop PC.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to connect to a controller with a laptop PC.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JohnBoehmer
    JohnBoehmer
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1505 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to connect to a controller with a laptop PC.

Picard Product_Support
‎2018-09-06 01:48 PM

Issue

Unable to connect to a NetController I using a terminal emulator program such as hyperterminal.

Unable to access controller webpage using MS Internet Explorer.

Environment

  • InfinityController
  • Internet Explorer
  • HyperTerminal
  • Terminal Emulator
  • Controller webpage.

Cause

The controller is configured with an IP address other than the factory default address.

The controller is configured with an unknown IP address.

The laptop PC is connected to the wrong port on the controller.

Resolution

To determine what IP address the controller has been configured for

  • Start a LAN capture on the laptop PC using WireShark or EtherReal
  • Power cycle the controller.
  • Once the controller has reset it will send out an gratuitous ARP packet that will contain the controllers IP address.

Second Generation Controllers

  • Connect a PC directly to the controller alone with a single ethernet cable.
  • Verify that the connector cable is connected to the correct port on the laptop PC (Do not use a USB Media convertor)
  • Verify that the connector cable is connected to the correct port on the Controller.
  • Verify that the IP setting on the PC and the IP setting of the controller are within the same subnet.
  • If Web Server Security is enabled  on the controller you must use https:// rather than http:// before the IP address.
  • If the controller has an IP reset button
    • Hold it down for 60 seconds to restore the factory default IP address.
    • Change the IP setting on the PC's network interface to 169.254.1.2
    • Attempt to access webpage using the default address  169.254.1.1
  • If the controller will not come on line reflash the firmware using RoamIO or Cyberstation. 
  • Determine if the Web TCP port was changed from the default

Note:

  • A controller does not necessarily have to show up as being online in CyberStation in order to be flashed.
  • If this will not work try bringing the controller into Cyber on a new test database, then reflashing.    

First Generation controllers                                              

  • Verify that the serial cable adapter has the correct pin configuration. 
  • Verify that the cable adapter is not damaged or defective.
  • CX9200 Ensure that the pins on the EPROMS that may have been switched from Infinity to Continuum are not bent
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5218
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore