Unable to backup objects to flash ACCFlashFailure Error seen
  • Unable to backup objects to flash ACCFlashFailure Error seen
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • AdamSteele
    AdamSteele
  • Alan_Wood
    Alan_Wood
‎2018-09-06 10:07 AM
Last Updated: Sisko DavidChild Sisko ‎2019-11-18 06:59 AM
Controller fails to backup to flash. See error message "Unable to backup objects to flash ..."
ACCStatusFlash variable should be ACCFlashValid not ACCFlashFailure
Andover Continuum
  • Continuum Controllers
  • NetController 2, bCX9640, bCX4040
A Program or Function in the Controller is corrupt and cannot be compiled or is blank and does not have any Plain English code in it.
  1. Go to the config page (Controller Configuration)
  2. Clear database backup
  3. Fix up or delete the offending programs
  4. Re-attempt to save the database to flash
Tags (3)
  • 14207
  • DavidShore19
  • failed
100% helpful (3/3)