Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Unable to assign output channels on a some b3 series controller under an AS

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to assign output channels on a some b3 series controller under an AS
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • PeterEdvik
    PeterEdvik
  • Dave_Shore
    Dave_Shore
  • StephenYang
    StephenYang
  • DavidFisher
    DavidFisher
  • Robert_Davis
    Robert_Davis
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3064 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to assign output channels on a some b3 series controller under an AS

Product_Support
‎2018-09-06 12:28 PM

Last Updated: PeterEdvik Champion ‎2020-06-04 06:23 AM

Issue

Unable to assign output channels on a some b3/i2 series controller under an AS.

CCT(Continuum Conversion Tool) unable to assign channel with error "Could not find channel" in the conversion report.

When creating an output channel, that is out of range, the workstation error is "Could not find channel"
eg. if output channels 15 or 16 (on b3810) are assigned

Product Line

EcoStruxure Building Operation

Environment

  • AS
  • ES
  • b3, i2
  • Expansion Module
  • xPD04, XPD02, xPA04, xPA02

Cause

b3/i2 series expansion channels are software limited in line with the maximum xP module capacity

The maximum b3/i2 expansion current available is 180mA, so some combinations of 2 xP modules are not supported, see below

2019-10-14_12-01-48.jpg

 

Resolution

Both input and output channels are limited in line with the allowable xP expansion units that can be added.
For example a maximum of 6 xP output channels can be added to b3/i2920, b3/i2810, b3/i2814, b3/i2850, b3/i2851 & b3/i2853 controllers, (2 xPD/A04 Output modules is above the maximum power supply to xP units from the b3/i2 series controllers)

                                  Output Channels
              On board                               xP Modules   
b3920     1 to 16                                   18 to 22
b3810     1 to 8                                      9 to 14
b3814     1 to 8                                      9 to 14
b3850     1 to 4 (5 reserved)                  6 to 11
b3851     1 to 4 (5 reserved)                  6 to 11
b3853     1 to 4 (5 reserved)                  6 to 11

NOTE Continuum did not limit the channel numbers, thus unsupported configuration could be installed and in some cases these may work. This can cause an issue during an upgrade/conversion.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 7696
  • channel
  • create
  • created
  • DavidShore19
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore