Unable to access ES or AS after setting a new Domain as the default domain
  • Unable to access ES or AS after setting a new Domain as the default domain
  • Jonas_Brissman
    Jonas_Brissman
  • CraigEl
    CraigEl
  • Derrick_Ratliff
    Derrick_Ratliff
  • Sacco
    Sacco
‎2018-09-06 10:23 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-19 08:09 PM
  • Building Operation Automation Server Premium (AS-P)
If you set a domain as a default domain before logging in through that domain, it is possible that you do not have users set up and therefore will be locked out of the system.
  1. Open Building Operation Workstation
  2. Enter a Username and password for the Local domain or another previously functional domain
  3. Set the Domain as "Local", please note that this is case sensitive.
  4. Select the correct Server
  5. Log in
  6. Change the default domain back to Local until you have successfully logged in using the new domain.