Troubleshooting Web Client login failures

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting Web Client login failures
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • PeterEdvik
    PeterEdvik
  • AdamSteele
    AdamSteele
  • David_Kendrick
    David_Kendrick

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4109 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting Web Client login failures

Guinan AdamSteele Guinan
‎2022-01-31 10:20 PM

Last Updated: Janeway PeterEdvik Janeway ‎2022-07-12 11:42 PM

Issue

Unable to log in to Web Client. After filling in the username and password and clicking "Sign In" the Sign In box disappears and the Username, Password, and Language Box are shown.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Server
  • Security Expert Web Client
  • Security Expert SOAP

Cause

Configuration issues are usually related to a mismatch between SOAP and Web Client security settings.

Resolution

Commonly this problem is resolved after re-installing SOAP and Web Client then rebooting the machine. If this does not resolve the problem then continue to check the below troubleshooting steps and gather information for support if those steps do not resolve the problem.

 

  1. Is everything on one machine or are the various components spread across a number of machines?
    1. If so, where is SQL, Security Expert Server, SOAP, Web Client, and Security Expert Client installed?
    2. If different machines, provide these details to support, which components are on each and what Operating System (OS) is installed.
  2. Are you using the HTTP connection for SOAP or HTTPS?
    1. If HTTPS and SOAP are on the same machine as Web Client then try using the HTTP port.
    2. Either re-install SOAP and Web Client using the HTTP option instead of or:
      1. Browse to the soap.connect.php located at C:\inetpub\wwwroot\SecurityExpertWebClient\include. 
      2. Edit it using e.g. Notepad and change HTTPS to HTTP and change the port to 8030 so the Web Client uses HTTP to communicate with the SOAP service.
      3. Then in IIS Manager restart the SecurityExpert and SecurityExpertWeb services.
  3. If a hardware or software firewall is being used, test the connection without these enabled.
  4. If Chrome is the browser being used then test with another browser such as Internet Explorer, Microsoft Edge, or Firefox.
  5. Confirm that all Security Expert services are running and started.
  6. Confirm the SOAP prerequisites have been installed for your Operating System (OS). See the Enabling the Required Windows Features section in the SX-SOAP Security Expert - SOAP Service - Installation Guide. In this document, there is a heading with instructions for each supported OS.
  7. Confirm that a Windows local admin user has been used to install all components. If in doubt, re-install Security Expert, then SOAP, then Web Client.
  8. Confirm if Security Expert was installed with Windows Authentication selected, if so then SOAP will need to have this option enabled as well during its installation.  Determining Security Expert authentication settings after installation 
  9. Confirm that you have adequate concurrent client licenses available on your Security Expert license. SOAP uses one of these when connecting to the Data service and if none are available the SOAP connection will fail.  See Unable to log in to Security Expert Web Client - 'Too Many Connections'
  10. The Microsoft Visual C++ 2015-2019 Redistributable Package is a requisite install for Web Client. Web Client installs this as part of the setup, confirm that this was installed.
  11. Check the Windows Event Logs for Security Expert errors. Open Windows Event Viewer:
    1. browse to Windows Logs > Application. Review logs and save all events to file. Provide this to Product Support if raising a support case.
    2. browse to Applications and Services Logs > Schneider Electric Security Expert. Review logs and save all events to file. Provide this to Product Support if raising a support case.
  12. Reboot machine after re-installation of SOAP or Web Client.
    1. If SOAP was re-installed then also re-install Web Client.

Please provide findings and responses to the above steps through to your local support channel for additional assistance should the problem continue.  

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (7)
  • Find more articles tagged with:
  • AdamSteele22
  • AdamSteele24
  • DavidKendrick22
  • login
  • security expert
  • users
  • webclient
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of