Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Trouble running programs on CyberStation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Trouble running programs on CyberStation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • JohnBoehmer
    JohnBoehmer

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1964 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Trouble running programs on CyberStation

Picard Product_Support
‎2018-09-10 04:58 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:41 PM

Issue

Every so often one or two programs on the Continuum workstation stop working.

Editing the program results in: A Cached Program cannot be opened while it is being written.

Product Line

Andover Continuum

Environment

  • CyberStation
  • WebClient
  • Continuum Programs

Cause

  • CyberStation was not installed properly.
  • Too many demands are being placed on the workstation.

Resolution

If the problem results from a problem with the installation of Continuum Cyberstation, refer to Problems installing Continuum.

Once Continuum has been properly installed, the problem may result from placing to many demands on the Continuum workstation.  Some questions that should be asked are...

  • How many programs are being run on the Cyberstation concurrently.
  • The default setting for Run on any workstation when a workstation program in created is false. This property should be checked for all workstation programs whether they must be run from another workstation or not. This setting can be found in the Program properties editor.
  • An a cached program cannot be opened while it is being written error may occurring when a report program is writing to disk.
  • Verify that the Cyberstation PC conforms to the Continuum Compatibility Matrix for the Continuum version.
  • How many PE programs are running on this workstation, how complex are these programs and are high level commands such as: Rotate, Run, Shell, OpenFile, OpenList, GetName, GetObject being used frequently.
  • How many report programs are running concurrently. 
  • Is the report workstation 100% dedicated to running reports and nothing else; no alarm reporting, no schedules, no extended log downloading, no Access server functions?
  • Is the workstation hardware and operating system sufficient for the work CyberStation is expected to do.
  • Managing these demands may involve sharing the reporting load over several CyberStations and/or adjusting the timing of processor intensive programs so that the workstation is executing fewer tasks at any given time. 
  • In some cases program performance may be impaired due to insufficient memory allocation. See Getting a Smart Heap error when starting Cyberstation or not all processes start and Cyber doesn't o....
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5330
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore