Trend log stops working in TAC Xenta
  • Trend log stops working in TAC Xenta
  • RobertAndriolo
    RobertAndriolo
  • Jonas_Brissman
    Jonas_Brissman
  • LeeCravens
    LeeCravens
  • sesa150555
    sesa150555
‎2018-09-06 10:54 AM
Last Updated: Picard RobertAndriolo Picard ‎2023-03-20 04:24 PM
Specific Trend log stops working in TAC Xenta
Get estimated values in some trend logs; others are working
Trend log is not retrieved from TAC Xenta
TAC Vista
  • TAC Xenta 301
  • TAC Xenta 302
  • TAC Xenta 401
  • TAC Xenta 282
  • TAC Xenta 283
The issue can be that there is a "Non value" in the log. For example, if you are logging an expression block with division in it and there is a division by 0. This seems to lock the trend in TAC Vista, and no other values can be collected.
In the properties for the log, click on erase log. This will delete all values in the device.
Open your menta and make sure that there is no possibility of division by 0.