Top 10 Steps for Troubleshooting Cyberstation and webClient issues

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Top 10 Steps for Troubleshooting Cyberstation and webClient issues
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6408 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Top 10 Steps for Troubleshooting Cyberstation and webClient issues

Picard Product_Support
‎2018-09-11 06:06 PM

Last Updated: Admiral Alan_Wood Admiral ‎2025-11-24 11:14 AM

Issue

There are many issues that can happen at Cyberstation and methods are needed to troubleshoot.

Product Line

Andover Continuum

Environment

  • Cyberstation

Cause

There are software updates and environmental reasons for issues coming from Cyberstation and there are a number of tools to help troubleshoot.

Resolution

This guide covers both software and hardware troubleshooting steps for Cyberstation and webClient issues. Use these methods and tools to diagnose problems:

  1. Determine Scope
  • Is the issue isolated (one workstation) or system-wide (multiple workstations)?
  • Isolated issues may relate to:
    • Installation problems
    • Windows OS or hotfixes
    • Hardware failures
  1. Check Continuum Compatibility
  • Verify versions of:
    • Continuum Service Packs
    • Windows OS (including Service Packs)
    • Microsoft SQL Server
    • Internet Browser
    • webClient
  • Software and Firmware Compatibility Matrix Version 2.03 
  1. Review Cyberstation Error Messages
  • Look for error messages displayed on screen.
  • Access help:
    • Press F1 in Cyberstation → Index → Type “Error” → Select “Error Messages”
    • Locate Cyberstation error messages
      How do you locate error messages in Cyberstation?

    4. Check Windows Event Viewer

  • Look for errors or event IDs at the time of the issue.
  • Use logs to:
    • Search online for solutions
    • Share with support
  • Sharing Windows Event Logs for Troubleshooting Purposes 
  1. Verify Windows Updates
  • Were any Service Packs or hotfixes recently applied?
  • List all updates:
    • Windows: How to List All of the Windows and Software Updates Applied to a Computer
  1. Check Installed Software
  • Review recently installed programs:
    • Windows XP: Control Panel → Add/Remove Programs
    • Windows 10: Control Panel → Programs and Features
  1. Scan for Viruses/Malware
  • Ensure Anti-Virus and Malware tools are updated.
  • Run full scans to clean infected PCs.
  1. Inspect Hardware
  • Common failure points:
    • Memory: Use BIOS diagnostics
    • Hard Drive: Run CheckDisk; reformat if needed
    • NIC (Network Interface Card): Swap if faulty
    • Graphics Card: Update drivers or replace
    • Use Windows Device Manager Look for devices with an exclamation point.
      Error codes in Device Manager in Windows
  1. Gather System Information
    • System Info (Msinfo32): Description of Microsoft System Information (Msinfo32.exe) Tool 
  1. Restore Point or Reinstall
  • Use Windows Restore Point (XP, Vista, 7): What is System Restore?
  • If unsuccessful:
    • Reformat hard drive if necessary and Reinstall Cyberstation or Windows OS
Labels (1)
Labels:
  • Andover Continuum
Tags (10)
  • Find more articles tagged with:
  • 6417
  • AlanWood19
  • AlanWood25
  • andover
  • continuum
  • cyberstation
  • internet explorer
  • troubleshooting
  • webclient
  • workstation
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore