Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Time Synchronization of Xenta programmable controllers under Automation Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Time Synchronization of Xenta programmable controllers under Automation Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1553 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Time Synchronization of Xenta programmable controllers under Automation Server

Picard Product_Support
‎2018-09-11 03:46 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:35 PM

Issue

How is the time synchronized between the Automation Server and Xenta Programmable Controllers?

If the time synchronization is offline, what can be done to correct this?

Product Line

EcoStruxure Building Operation

Environment

  • Automation Server
  • Building Operation Workstation

Cause

Time Synchronization occurs between the Automation Server and the Xenta Programmable controllers during two events:

  1. When the Xenta programmable controller is commissioned.
  2. Periodically the time is synchronized (default 10 minutes, but configurable).

For the time synchronization to work properly it is critical to ensure that the time zone of the automation server is correct and the date/time of the automation server is correct.

Resolution

Walk through these steps to troubleshoot the synchronization of the Automation Server and Xenta controllers.
 
  1. Check that all Xenta devices are at software revision 3.74 or higher
  2. Check the local time of the Xenta programmable controller by accessing the properties of the programmable controller and using the "Xenta" property tab group. The local time is listed there.
  3. Check the time zone of the automation server. By default the "Factory time zone" needs to be changed for proper operation.
  4. Check the server time of the Automation Server in the Basic property tab of the Automation Server.
  5. Check Time Synchronization Interval setting of the LonWorks Network object under the advanced tab in the Xenta General section. Default is 10 minutes.
  6. Either wait for the interval to elapse or manually commission the controller to synchronize the time and check the local time of the controller to ensure it completed properly.

 

Note: Keep in mind that the time displayed time in Workstation reflects the time zone of the local machine. If you are logging into an Automation Server in a different time zone, the alarms and events will be displayed in your local time, not the time of the Automation Server's time zone. For more information on Time settings and Synchronization see Time Synchronization of the ES and AS.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 13079
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of