Issue
Should the Touchscreen "Time Master" setting still be enabled when the Touchscreen is connected to a Xenta 555?
Product Line
Satchwell MicroNetEnvironment
- Satchwell MicroNet
- Xenta 555
Cause
In standalone configurations, the Touchscreen is typically designated as the "Time Master" to ensure consistent time synchronization across connected controllers. When integrated with a Xenta 555, users may question whether this setting remains necessary.
Resolution
Yes, the Touchscreen should still be configured as the "Time Master" even when connected to a Xenta 555. The time synchronization behavior remains unchanged:
- The Touchscreen will broadcast the time every 10 minutes by default.
- This ensures that all connected controllers maintain accurate and synchronized time settings.