Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

The device is applicationless, or is not associated with a program record. (Subsystem: NS, #5)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The device is applicationless, or is not associated with a program record. (Subsystem: NS, #5)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2721 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The device is applicationless, or is not associated with a program record. (Subsystem: NS, #5)

Picard Product_Support
‎2018-09-07 03:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:17 PM

Issue

NS5.bmp

The device is applicationless, or is not associated with a program record. (Subsystem:  NS, #5)

The target device does not have a valid application loaded. To correct this problem, right-click on the device and select the "Load" option. Then, if necessary, repeat this operation.

The device was discovered to be applicationless, or not associated with a program. If you encounter this error, load the application into the device. For host-based nodes, ensure that the host application is running

Product Line

Other, TAC Vista

Environment

  • LNS
  • LonMaker
  • Vista
  • NL220

Cause

Interrupting a download can cause the download to fail and render the controller applicationless.  Also, a corrupt Menta file can sometimes successfully download, but cause the controller to go into an applicationless state.

Resolution

An application must be downloaded through Menta while directly connected to the controller through the RS-232 serial port.  A blank Menta file with just one PVR is sufficient to restore an application to the controller and allow it to be downloaded; however, downloading the actual Menta file is better because it can expose parsing errors in the Menta file that need to be fixed before downloading it through the System Plug-in again.

In some cases, an attempt to direct download can not establish communications to the controller and "timeout". In this event, download a new .mot file to the system using the Download Wizard. Instructions are located in Instructions on how to download an .MOT file into a Xenta Programmable controller.

If the Download Wizard  is not able to establish communications with the device, the program should first be cleared using a Xenta Hardware Reset Tool. You can make one by following the instructions located in Xenta Controller Will Not Download / How to Clear the Xenta Application. If the Xenta firmware is older than 3.61, the method to clear the Xenta application is to power cycle the controller 10 consecutive times.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4121
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore