TAC Xenta servers are going offline in TAC Vista

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TAC Xenta servers are going offline in TAC Vista
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Jonas_Brissman
    Jonas_Brissman
  • HenrikTarpgaard
    HenrikTarpgaard
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3256 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TAC Xenta servers are going offline in TAC Vista

Janeway Jonas_Brissman Janeway
‎2019-11-26 12:48 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-02-28 02:50 PM

Issue

Windows update KB4519976 causes all Xenta servers to go offline in TAC Vista every few minutes.

Product Line

TAC Vista

Environment

  • TAC Vista Server
  • Microsoft Windows 7 or Microsoft Windows 2008 Server
  • Xenta 500
  • Xenta 700
  • Xenta 900

Cause

After the Windows update, KB4519976 is installed, the SSL handshake behavior is changed. This affects TAC Vista and its communication with the TAC Xenta server.

Resolution

There are two workarounds available at the moment.

Solution 1:

Uninstall Windows update KB4519976

Solution 2:

Turn off SSL for the communication between TAC Vista and the TAC Xenta server using the registry setting shown below. This means that only the login will be encrypted when TAC Vista is communicating with the TAC Xenta servers.

  1. Run the utility TacosTweak.exe, located in the program folder where TAC Vista is installed.

    SSL.png
  2. Set "Only use SSL for login to TAC Xenta Servers(5xx/7xx)" to 1 to run the communication between TAC Vista and TAC Xenta servers without SSL.
  3. Restart the TAC Vista server for the changes to take effect.
Labels (1)
Labels:
  • TAC Vista
Tags (5)
  • Find more articles tagged with:
  • HenrikTarpgaard20
  • JonasBrissman19
  • KB4519976
  • RobertAndriolo22
  • Xenta Servers
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of