TAC Xenta does not show the same time as TAC Vista.
  • TAC Xenta does not show the same time as TAC Vista.
  • RobertAndriolo
    RobertAndriolo
  • PeterLarsen
    PeterLarsen
‎2018-09-06 03:17 PM
Last Updated: Picard RobertAndriolo Picard ‎2020-07-02 05:49 PM
TAC Vista
  • TAC Vista Workstation
  • Xenta programmable controllers
The time in the Xenta comes from the Vista server. However, it can be adjusted for time zones and daylight savings time settings.
Check daylight savings time and time zone settings in TAC Xenta. The setting should be the same as in the Operating Unit (if they are in the same time zone).
Check if a PVR object name XENTASYSREG is in the Menta application with a value of 2.
This inverts Europe daylight setting and causes the controller to adjust its time.
Note! This is NOT the regional settings on your PC, but the setting in the Vista object in your DB.