What TAC Xenta I/O modules could act as a Stand-Alone LonWorks device?
EcoStruxure Buildings Operation, TAC Vista
  • LonWorks TP/FT-10 Network
  • TAC Xenta 420A
  • TAC Xenta 421A
  • TAC Xenta 422A
  • TAC Xenta 450A
  • TAC Xenta 451A
  • TAC Xenta 452A
It is only TAC Xenta 421A, 422A, 451A, and 452A that can act as Stand-Alone LonWorks devices.
It is only TAC Xenta 421A, 422A, 451A, and 452A that can act as Stand-Alone LonWorks devices. TAC Xenta 400 I/O modules without -A, will not work as Stand Alone LonWorks devices. Once communication has been established with the Xenta I/O module the green status led will flash on for 1 second every 10 seconds indicating it is in Stand-Alone mode.
In Building Operation, the Lonworks devices list will show devices without an "A" after it. This may lead to the wrong conclusion that these devices can be added as stand-alone devices, but that is not the case. These devices are listed so that they can be added manually to a programmable Xenta device as an IO module.