Issue
There is no quick and efficient way to configure a TAC Xenta 102-AX controller after adding it to a LonWorks Network in Building Operation.
Product Line
EcoStruxure Building Operation
Environment
Building Operation Workstation
Cause
The TAC Xenta 102-AX controller is typically configured using the LNS plug-in that is currently not available in version 1.4.0 and newer.
Resolution
As an alternative to the LNS plug-in, the graphic page available on the Community [1] can be used. This zip file contains the TGML graphic, binding template, and a full import file with a Xenta 102-AX that is already bound.
[1] Xenta 102-AX SXW TGML Plugin v1.6.1 (SBO 1.8.0 to 1.9.3)