Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

StruxureWare ETL tool locks up or takes a long time while loading sources

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • StruxureWare ETL tool locks up or takes a long time while loading sources
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4488 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

StruxureWare ETL tool locks up or takes a long time while loading sources

Product_Support
‎2018-09-10 04:16 AM

Last Updated: CraigEl Champion ‎2022-08-08 05:56 PM

Issue

The ETL job configuration tool freezes when running the load sources task under the mappings tab.

Product Line

EcoStruxure Building Operation

Environment

  • Extract Transform Load Administration Tool (ETL)
  • Power Manager for SmartStruxure
  • EcoStruxure Web Services (EWS)
  • Enterprise Server
  • Automation Server

Cause

The ETL default HTTP query size is set to 10 which in some cases can impact the performance of the tool.

Resolution

Make sure that you read through Energy Expert (Power Manager for SmartStruxure): Best Practices. This article will provide a lot of tips to avoid issues or improve system performance.

ETL locks up while loading sources

Adjust the HTTP query size to a higher value. This will reduce the number of queries between ETL and the SBO Server.

  1. Close ETL.
  2. Go to the location where ETL is installed. The default path is C:\Program Files\Schneider Electric\ETL X.X (SBO to PME).
  3. Under the Jobs folder there is a project file named "JOB_ETLProjectName.xml". Open this XML file with a text editor.
  4. Search for the setting called "ContainerQueryBatchSize". It is set to 10 by default, change it to 100 and save the job.
  5. Open the ETL user interface again and try running the Load Sources task. The folder count at the bottom of the screen will increase slower then before because each call is gathering ten times as much data.

Note: If the ETL tool locks up again with the query size set to 100, try other values until it is able to complete the task such as 50, 25, etc.


ETL takes a very long time to load sources

When dealing with very large systems it can take hours for ETL to search through the entire database for all trends. To help reduce the searching time filters can be created to restrict what is exposed to EWS.

  1. Go to the System folder EcoStruxure Web Services > EWS Server Configuration. Click on the Filter Hardware Folder tab.
  2. Under the "Filter Hardware Folder by Path" section, click on the green addition symbol. In the pop up window, name the path filter and click create.
  3. Select the newly created filter path and click on the edit symbol. Enter the path of the folder or item in the database that you want to exclude from EWS. Click Okay.
    Note: All filter paths created here will NOT be searched by the ETL tool.
  4. Save changes.
  5. Once the ETL tool has loaded sources and the project has been created, the EWS filters may be removed.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 18672
  • finish
  • stops
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore