Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Steps for replacing a BACnet B3 controller and things to consider.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Steps for replacing a BACnet B3 controller and things to consider.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JonGreen
    JonGreen
  • Clifton_eakes
    Clifton_eakes
  • sesa139513
    sesa139513
  • Carl_Slack
    Carl_Slack
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4469 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Steps for replacing a BACnet B3 controller and things to consider.

Picard Product_Support
‎2018-09-06 02:35 PM

Last Updated: Picard RobertAndriolo Picard ‎2019-09-04 05:32 PM

Issue

Steps for replacing a BACnet B3 controller and things to consider.

Product Line

Andover Continuum

Environment

Continuum b3xxx Controller

Cause

Steps for replacing a BACnet B3 controller and things to consider.

Resolution

Steps for replacing a B3 controller and things to consider.

Use these steps when replacing a B3 controller from brand new stock, it is relatively straight forward.

  1. Physically disconnect power and MS/TP data cables from existing B3 Controller.
  2. Remove existing B3 Controller.
  3. Install replacement B3 Controller.
  4. Pull the battery tab on replacement B3.
  5. Connect MS/TP data cable to the replacement B3 controller.
  6. Connect power to the replacement B3 controller.
  7. Edit the B3 controller object in Continuum on the infinity side.
  8. On the Runtime tab enter the Serial Number of the new replacement B3 controller and click Apply.
  9. Click refresh until B3 controller returns Online.
  10. Reload the B3 Controller.
  11. Verify existing points and programs are running correctly.
  12. Perform a “Backup to Flash” operation on the B3 controller.
  13. Perform “Send to Database” operation on B3 controller from BACnet view.

One scenario, for example, is the Replacement B3 controller came from a different job that has previously been programmed and has a valid flash backed up onto it. If installed on the new network, when powered up will start trying to communicate with controllers it has routing tables for. Could potentially cause issues on the new network. It is suggested that if you are replacing with a previously used controller from an old site with a valid flash backed up is to flush the controller out before applying to the new network. From a test machine with a test DB bring the controller online, this will require a BCX to do as well. Once the B3 is learned in and online, perform a reload to the controller and then a backup to flash. The only thing that will be reloaded will be the system variables.

Another thing to think about is let's say you've already replaced the B3 and sent it off to repair. You've got it back and now want to put it back to its original location. That one is very simple and following the replacement steps above will suffice. Just remember that step 8 above you would make sure the Bacnet Device ID and the serial number match for the original unit integration. But if you wanted to add a new B3 controller to the same site and use the repaired B3 as a newly installed controller, just remember that the previously replaced B3 will have
the Bacnet Device ID of the repaired B3 and you'll have to make sure that when manually creating a new B3 with the repaired B3 you'll have to make a new Bacnet Device ID that is unique.

Rules to remember:

  1. Flush out used B3 controllers before adding to an existing MS/TP network or replacing a defective B3
  2. Bacnet Device ID's must be unique for each given BACnet network

 

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 3549
  • CliftonEakes19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore