Issue
What register type should be used for the type called INT64 in the documentation
Product Line
EcoStruxure Building Operation
Environment
- EcoStruxure Building Operation
- Modbus
- PM Energy meter
Cause
It is not clear what Modbus register type should be configured for INT64
Resolution
For reading the INT64 on this range of power meters the register definition you need to apply is the "64 bit signed swapped".
Note that this register type is not available in Building Operation versions earlier than 1.5. For further information on Modbus Register Types see the Point and Value Configuration EBO Webhelp topic