Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SmartStruxure Lite MPM BACnet client capabilities

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SmartStruxure Lite MPM BACnet client capabilities
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2549 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SmartStruxure Lite MPM BACnet client capabilities

Picard Product_Support
‎2018-09-10 02:09 PM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:56 AM

Issue

A third party BACnet system is able to host  values from a SmartStruxure Lite MPM but an MPM does not seem able to host values from another BACnet system or device.

Environment

BACnet

MPM-VA

MPM-UN

MPM-GW

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

SmartStruxure Lite Managers have full BACnet server capabilities, however BACnet client functionality is not native to the MPM and is currently only available through Lua programming.

Resolution

Integrating SmartStruxure Lite™ Managers with third-party BACnet server devices requires a BACnet client script. A sample script (download here) can be used to perform read and write operations to other devices via BACnet IP, however, a few tips and limitations must be taken into consideration before deployment on site.

NOTE1: The delay at the beginning of the script (if scl.sysclock() > 90 then) must not be removed or modified. Otherwise, the MPM will keep rebooting endlessly and would require restoring its factory defaults before gaining access to Building Expert again.

NOTE2 : The more points used in the script, The higher the MPMs CPU% Usage will be and the less responsive the MPM will be. Therefore, it is recommended to only read/write the necessary points and not all the points on the third party devices. Also, if some points are more important that others, the polling time can be increased to 60 seconds for example.

 

NOTE3: The more objects you have on the MPM, the less room you have for BACnet points. PGs, Trends and Events consume a substantial amount of CPU Usage so it is important to keep an eye on it as you add more points in the script.

statistics.png

 

NOTE4 : Run the script every 5 seconds or more if possible

lua-editor.png

 

Limitations:

- Reading/Writing to Multi State Values (MSV) is not supported

Labels (1)
Labels:
  • EcoStruxure Building Expert
Attachments
Tags (2)
  • Find more articles tagged with:
  • 15355
  • bacnetip
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore