SmartStruxure - How many S-Cables can be used when connecting additional rows of I/O modules?
  • SmartStruxure - How many S-Cables can be used when connecting additional rows of I/O modules?
  • sesa139513
    sesa139513
  • Cody_Failinger
    Cody_Failinger
  • sesa125819
    sesa125819
‎2018-09-11 03:56 AM
Is there a limit to the number of S-Cables which can be used when connecting additional rows of I/O modules?
S-Cables
I/O modules
Rows
extending
SmartStruxure is being installed into an existing building and the current controllers are split into several rows.
A maximum of 5 cables can be used on an IO back plane. You can serially connect up to 2 S-cables in a row to extend the length.
This information was located in StruxureWare Building Operation Help – Installation Instructions - Terminal Base TB-PS-W1
  • 13368
100% helpful (1/1)