Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SmartStruxure COV limits and re-subscription questions.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SmartStruxure COV limits and re-subscription questions.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Benji
    Benji
  • Cody_Failinger
    Cody_Failinger
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2337 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SmartStruxure COV limits and re-subscription questions.

Picard Product_Support
‎2018-09-11 09:07 AM

Issue

What happens when a device that SmartStruxure has COV subscriptions with goes OFFLINE for a while and then comes back ONLINE?

Environment

ES

AS

BACnet devices

Cause

Documentation

Resolution

QUESTION:

What is the limit on number of COV subscription AS/ES support.

ANSWER:

There is no hard limits in the AS/ES for number of COV subscription, the server is limited only by resources.

QUESTION:
How often does the Automation Server subscribe (sends the subscription requests) for the very first time to the other devices?

ANSWER:
When the subscriptions are first established they are sent immediately to the devices, for example when you save a PE script program any COV created as a result of compiling the program are sent immediately to the device.

QUESTION:
In the case that the other device (the gateway) restarts or goes OFFLINE, how does the Automation Server handle the sending of the re-subscription requests?

ANSWER:
If a renewal fails due to device offline, it will be retried every minute indefinitely until it succeeds or the subscription is canceled.
So if the device goes offline for a while some of the re-subscriptions will fail and will be re-tried once a minute, when the device is back, within a minute all the failed re-subscriptions will be sent again.

QUESTION:
Can the COVSubscriptionLifetime and the COVTimerPeriod  be set in the AS? or is it only in the ES

ANSWER:
They can be set in both the ES and the AS by editing the server.properties file in versions of SBO prior to 1.8.1

In SBO 1.8.1 and above, the settings can be accessed from the BACnet interface manager.



QUESTION:
Where is the server.properties file located in the server file system?

ANSWER:
AS: /opt/tac/etc (1.4.1 and below)
AS: /opt/sbo/etc (1.5.0 and above)

/opt/tac/db (1.4)

 

/var/sbo/db (1.5)
/opt/tac/db (1.4)

 

/var/sbo/db (1.5)
/opt/tac/db (1.4)

 

/var/sbo/db (1.5)

ES:  "C:\Program Files\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\etc\
 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 16845
  • losing
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore