Site License is not working after upgrading to Vista 5.1.4 through 5.1.7
  • Site License is not working after upgrading to Vista 5.1.4 through 5.1.7
  • David_Kendrick
    David_Kendrick
  • Sacco
    Sacco
‎2018-09-10 03:39 AM
Last Updated: Admiral David_Kendrick Admiral ‎2022-08-09 08:13 AM
Site License is not working after upgrading to Vista 5.1.4 or newer.
TAC Vista
Vista License
The path to the License Server (lmgrd.exe) and License File (Licensename.lic) is incorrect because the default Vista installation folder changed from TAC in 5.1.3 and older to Schneider Electric 5.1.4 and newer.
  1. Stop and close TAC Vista Server, Workstation, etc.
  2. Open the LMTOOLS utility from the Start menu: All Programs/Schneider Electric/TAC Tools 5.x.x/LMTOOLS
  3. Under "Config Services Tab", ensure the path to licenses file is correct ,C:/Program Files/Schneider Electric/License.
  4. Under "Start/Stop/Reread" tab, check "Force Server Shutdown" box. In order click, "Stop Server", "Start Server", "Reread License File". You should receive a message stating the Reread License File Completed.
  5. Start any TAC application other than Vista Server (for example: TAC Menta). You will be prompted to "Specify the License Server System" or "Specify the License File". Select "Specify the License Server System" and enter the computer name. Alternatively, If the License Server resides on the local machine, you may type "localhost" as the computer name.
If the above is unsuccessful, follow the full steps in the resolution of TAC Vista 5.0 to 5.1.7 license does not work after installation which will also correct the path name to Schneider Electric.