Issue
In scenarios where no Digital Input (DI) channels are available, users may need to simulate digital input functionality using Analogue Input (AI) cards.
Product Line
Satchwell BAS & SigmaEnvironment
Sigma Analogue Input cards.
Cause
Sigma Analogue Input cards are not designed to function as Digital Input cards. However, a workaround can be implemented to simulate digital input behavior using available analogue channels.
Resolution
To configure an Analogue Input to behave like a Digital Input:
-
Create an Analogue Input Object
- In Sigma System Manager, define an Analogue Input object using a free point number.
-
Configure a Lookup Table
- Create a lookup table to translate analogue values into digital states:
Input Output 0 1 15 0 20 0 - Assign this lookup table to the Analogue Input object.
- Create a lookup table to translate analogue values into digital states:
-
Add Short Text for Display
- Create a Short Text (e.g.,
On/Off = %2.f) to represent the digital state. - Link this Short Text to the Analogue Input object.
- Create a Short Text (e.g.,
-
Hardware Setup
- Fit a 1000-ohm resistor across the Analogue Input channel.
- This resistor acts in parallel with the digital input wiring.
-
Result
- When the connected digital input changes state, Sigma will interpret and display the result as either
1(On) or0(Off), effectively simulating a digital input.
- When the connected digital input changes state, Sigma will interpret and display the result as either
Notes
- This method is a workaround and should be used only when DI channels are unavailable.
- Ensure proper calibration and testing to avoid misinterpretation of analogue signals.