Sigma - Upgrading the DeviceCNF.rec and GenCNF.rec files.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Upgrading the DeviceCNF.rec and GenCNF.rec files.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1269 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Upgrading the DeviceCNF.rec and GenCNF.rec files.

Picard Product_Support
‎2018-09-06 02:01 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-20 05:52 PM

Issue

During an upgrade to Sigma 4.05 SEB, the User and Network device configurations may be lost. This typically occurs when the DeviceCNF.rec and GenCNF.rec files are not properly upgraded.

Product Line

Satchwell BAS & Sigma

Environment

Sigma 4.05 SEB

Cause

Sigma 4.05 SEB introduced changes to the format of the DeviceCNF.rec and GenCNF.rec files. If these files are not correctly upgraded, the system may lose general configuration data, including network and device settings.

Resolution

To ensure a successful upgrade and preserve configuration data, follow these steps:

  1. Shutdown Sigma Services

    • Close both the Sigma Client and Sigma Server on the Sigma 4.05 SEB machine.
  2. Prepare a Clean Data Folder

    • Use a clean Sigma 4.05 Data folder—this means a folder created during the original Sigma client/server installation.
    • Do not use complete Data folders from earlier Sigma versions.
  3. Copy Backup Files

    • Copy your site-specific Sigma backup files into the clean Data folder.
  4. Run the Upgrade Utility

    • Navigate to:
      C:\Sigma\Binutils\SigUpgrade.exe
      and run the SigUpgrade.exe utility.
  5. Verify File Updates

    • Check the following files in C:\Sigma\Data\:
      • DeviceCNF.rec
      • GenCNF.rec
    • Confirm that their file dates reflect the recent update.
  6. Restart Sigma Services

    • Start the Sigma Server and Sigma Client.
    • Verify that the configuration is intact and functioning as expected.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 4793
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore