Sigma - Requested Clients Window Shows a Remote Client as Being Off-line
  • Sigma - Requested Clients Window Shows a Remote Client as Being Off-line
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
‎2018-09-06 01:11 PM
Last Updated: Administrator CraigEl Administrator ‎2025-10-23 12:54 AM
The Requested Clients window in Sigma displays a remote client as being off-line, even though it is active.
Satchwell BAS & Sigma
Satchwell Sigma
This behavior is due to Sigma defect 3174, where the status shown in the Registered Clients window may be incorrect. The issue arises when the remote client is started before the local client, leading to a misrepresentation of its online status.
To resolve this issue, you have two options:
  1. Upgrade Sigma:
    • The defect was been corrected in Sigma release 4.05 SEB.
    • Upgrade the site to this release or any later version to permanently fix the issue.
  2. Workaround (if upgrade is not possible):
    • Shut down Sigma.
    • Restart the local client first, then start the remote client.
This sequence ensures accurate status reporting in the Requested Clients window.
  • Satchwell BAS & Sigma
Tags (2)
  • 6380
  • CraigEllis25