Issue
OPC values are visible via an OPC client on the local PC, but not accessible from another OPC client across the network.
Product Line
Satchwell BAS & SigmaEnvironment
- Sigma ModBMS
- Matrikon OPC Client
Cause
The DCOM settings on the OPC Server PC are not correctly configured for remote access.
Resolution
-
Configure DCOM Settings
Refer to the official Matrikon OPC documentation for detailed instructions.
👉 Download Matrikon OPC DCOM Configuration Guide -
Install Matrikon OPC Client
👉 Download Matrikon OPC Explorer -
Launch Matrikon OPC Explorer
- Navigate to Network Neighborhood
- Locate the OPC Server PC
- Select ModBMS-OPCserver
-
Create a New Group
- Right-click and choose Add Group
- Name the group as needed
- Add required tags
- Right-click and choose Add Group
-
Validate Tags
- Right-click the group
- De-select Use Async I/O
- The OPC values should now be displayed
- Right-click the group