Sigma – IC-SNP / IC3-SNP SubLAN / IAC LAN Controller Fault Finding
  • Sigma – IC-SNP / IC3-SNP SubLAN / IAC LAN Controller Fault Finding
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • sesa139513
    sesa139513
  • DavidChild
    DavidChild
  • sesa125819
    sesa125819
‎2018-09-06 10:45 AM
Last Updated: Administrator CraigEl Administrator ‎2025-11-09 05:57 PM
Fault Finding on an IC-SNP / IC3-SNP and associated IAC controllers.
Satchwell BAS & Sigma
  • IC-SNP
  • IC3-SNP
  • IAC controllers
Communication faults on the SubLAN may be caused by:
Cause Description
Incorrect LAN Termination Missing or improperly placed 120-ohm resistors can cause signal reflections and data corruption.
Biasing Misconfiguration Bias jumper not set to “D” (Full Biasing) can result in unstable idle voltage levels.
Faulty Controller Driver A single IAC controller with a failed RS-485 driver can hold the RX line low, blocking communication.
Corrupted gateway.txt Entries Invalid or misconfigured entries can prevent the IC-SNP from initializing communication properly.
Physical Layer Issues Damaged cables, poor connections, or incorrect wiring can interrupt signal transmission.
Power Supply Problems Inadequate or unstable power to controllers can cause intermittent or complete communication loss.
IC-SNP Hardware Failure Internal faults in the IC-SNP or IC3-SNP can prevent proper LAN operation.
Excessive LAN Length or Load Too many devices or long cable runs without repeaters can degrade signal quality.
Environmental Interference Electrical noise from nearby equipment can disrupt RS-485 signals.
1. Use of Alarm Manager
  • Access via Sigma default/backup server.
  • Review system messages (priorities 22–30) for controller-specific errors.
  • Look for messages like “Unable to Communicate with Controller ???”.
2. Troubleshooting gateway.txt File
Symptoms:
  • “Unable to open gateway.txt file” error.
Steps:
  1. Start with a minimal gateway.txt (1–2 entries).
  2. Use a known-good version from Exchange-On-Line.
  3. If errors persist:
    • Remove all entries except one.
    • Download and warm-start the controller.
    • Gradually reintroduce entries to isolate the faulty line.
3. Controller Not Responding
Single Controller:
  • Check local communication using Visisat and LIB-4-485.
  • Verify LAN wiring and power supply.
Multiple Controllers:
  • Indicates partial or full SubLAN failure.
  • Begin investigation at the IC-SNP.
4. IC-SNP Hardware Checks
Component Expected Behavior
Bias Jumper Set to D (Full Biasing)
Termination 120-ohm resistors at both ends
Channel 2 TX LED Flashes after warm-start (gateway.txt processing)
Channel 2 RX LED Flashes if receiving replies
RX LED Permanently On:
  • Indicates a faulty IAC controller driver disrupting LAN comms.
5. IC-SNP Retry Mechanism
  • Retries each controller 3 times before marking offline.
  • Sends error to Alarm Manager.
  • Retries offline controllers every 30 minutes (on the hour and half-hour).
6. Binary Chop Method for LAN Isolation
Purpose:
Efficiently isolate faulty segments or controllers.
Steps:
  1. Identify LAN midpoint.
  2. Disconnect twisted pair at nearest controller.
  3. Observe RX LED behavior:
    • LED Off: Fault lies beyond midpoint.
    • LED On: Fault lies before midpoint.
  4. Repeat by halving LAN again (25% or 75%) until fault is found.
7. Voltage Testing Guidelines
Use a DC voltmeter to measure:
Measurement Expected Voltage
+ve to 0V ~2.5 V
–ve to 0V ~0.15 V
+ve to –ve ~2.31 V
Note:
  • Negative voltages suggest LAN faults.
  • Compare readings across segments to identify anomalies.
8. RX LED Not Flashing at All
Possible Causes:
  • Faulty IC-SNP
  • Faulty SubLAN
  • Faulty Controllers
Steps:
  1. Disconnect LAN after first controller.
  2. Warm-start IC-SNP.
  3. Observe RX LED:
    • If flashing resumes, use binary chop to isolate fault.
    • If not, test cable and controller individually.
9. Cable Testing Procedure
  1. Disconnect both ends and separate cores.
  2. Measure resistance:
    • Between cores: ∞
    • Each core to earth: ∞
  3. Short cores at one end.
  4. Measure resistance at other end:
    • Between cores: ~0 Ω
10. Controller Testing
  • Use LIB-4-485 and Visisat Engineering software.
  • Confirm controller responds to direct communication.
Final Steps:
Once faults are resolved:
  1. Download full gateway.txt.
  3. Monitor Alarm Manager for new errors.
Labels (2)
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
Tags (5)
  • 12170
  • comms
  • CraigEllis25
  • iac420
  • iac600