Sigma – IC-SNP / IC3-SNP SubLAN / IAC LAN Controller Fault Finding

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma – IC-SNP / IC3-SNP SubLAN / IAC LAN Controller Fault Finding
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Cody_Failinger
    Cody_Failinger
  • sesa139513
    sesa139513
  • DavidChild
    DavidChild
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1775 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma – IC-SNP / IC3-SNP SubLAN / IAC LAN Controller Fault Finding

Picard Product_Support
‎2018-09-06 10:45 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-09 05:57 PM

Issue

Fault Finding on an IC-SNP / IC3-SNP and associated IAC controllers.

Product Line

Satchwell BAS & Sigma

Environment

  • IC-SNP
  • IC3-SNP
  • IAC controllers

Cause

Communication faults on the SubLAN may be caused by:

Cause Description
Incorrect LAN Termination Missing or improperly placed 120-ohm resistors can cause signal reflections and data corruption.
Biasing Misconfiguration Bias jumper not set to “D” (Full Biasing) can result in unstable idle voltage levels.
Faulty Controller Driver A single IAC controller with a failed RS-485 driver can hold the RX line low, blocking communication.
Corrupted gateway.txt Entries Invalid or misconfigured entries can prevent the IC-SNP from initializing communication properly.
Physical Layer Issues Damaged cables, poor connections, or incorrect wiring can interrupt signal transmission.
Power Supply Problems Inadequate or unstable power to controllers can cause intermittent or complete communication loss.
IC-SNP Hardware Failure Internal faults in the IC-SNP or IC3-SNP can prevent proper LAN operation.
Excessive LAN Length or Load Too many devices or long cable runs without repeaters can degrade signal quality.
Environmental Interference Electrical noise from nearby equipment can disrupt RS-485 signals.

Resolution

1. Use of Alarm Manager

  • Access via Sigma default/backup server.
  • Review system messages (priorities 22–30) for controller-specific errors.
  • Look for messages like “Unable to Communicate with Controller ???”.

2. Troubleshooting gateway.txt File

Symptoms:

  • “Unable to open gateway.txt file” error.

Steps:

  1. Start with a minimal gateway.txt (1–2 entries).
  2. Use a known-good version from Exchange-On-Line.
  3. If errors persist:
    • Remove all entries except one.
    • Download and warm-start the controller.
    • Gradually reintroduce entries to isolate the faulty line.

3. Controller Not Responding

Single Controller:

  • Check local communication using Visisat and LIB-4-485.
  • Verify LAN wiring and power supply.

Multiple Controllers:

  • Indicates partial or full SubLAN failure.
  • Begin investigation at the IC-SNP.

4. IC-SNP Hardware Checks

Component Expected Behavior
Bias Jumper Set to D (Full Biasing)
Termination 120-ohm resistors at both ends
Channel 2 TX LED Flashes after warm-start (gateway.txt processing)
Channel 2 RX LED Flashes if receiving replies

RX LED Permanently On:

  • Indicates a faulty IAC controller driver disrupting LAN comms.

5. IC-SNP Retry Mechanism

  • Retries each controller 3 times before marking offline.
  • Sends error to Alarm Manager.
  • Retries offline controllers every 30 minutes (on the hour and half-hour).

6. Binary Chop Method for LAN Isolation

Purpose:
Efficiently isolate faulty segments or controllers.

Steps:

  1. Identify LAN midpoint.
  2. Disconnect twisted pair at nearest controller.
  3. Observe RX LED behavior:
    • LED Off: Fault lies beyond midpoint.
    • LED On: Fault lies before midpoint.
  4. Repeat by halving LAN again (25% or 75%) until fault is found.

7. Voltage Testing Guidelines

Use a DC voltmeter to measure:

Measurement Expected Voltage
+ve to 0V ~2.5 V
–ve to 0V ~0.15 V
+ve to –ve ~2.31 V

Note:

  • Negative voltages suggest LAN faults.
  • Compare readings across segments to identify anomalies.

8. RX LED Not Flashing at All

Possible Causes:

  • Faulty IC-SNP
  • Faulty SubLAN
  • Faulty Controllers

Steps:

  1. Disconnect LAN after first controller.
  2. Warm-start IC-SNP.
  3. Observe RX LED:
    • If flashing resumes, use binary chop to isolate fault.
    • If not, test cable and controller individually.

9. Cable Testing Procedure

  1. Disconnect both ends and separate cores.
  2. Measure resistance:
    • Between cores: ∞
    • Each core to earth: ∞
  3. Short cores at one end.
  4. Measure resistance at other end:
    • Between cores: ~0 Ω
    • Each core to earth: ∞

10. Controller Testing

  • Use LIB-4-485 and Visisat Engineering software.
  • Confirm controller responds to direct communication.

Final Steps:

Once faults are resolved:

  1. Download full gateway.txt.
  2. Warm-start IC-SNP.
  3. Monitor Alarm Manager for new errors.
Labels (2)
Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
Tags (5)
  • Find more articles tagged with:
  • 12170
  • comms
  • CraigEllis25
  • iac420
  • iac600
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore