Sigma IC-Modbus - Reading 32 Bit Integer values from two 16 Bit registers.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma IC-Modbus - Reading 32 Bit Integer values from two 16 Bit registers.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2120 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma IC-Modbus - Reading 32 Bit Integer values from two 16 Bit registers.

Picard Product_Support
‎2018-09-06 12:11 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-07 05:33 PM

Issue

How to read a 32-bit integer value stored across two 16-bit registers using IC-Modbus.

Product Line

Satchwell BAS & Sigma

Environment

  • IC-Modbus
  • IC3-Modbus

Cause

Prior to firmware release 4.05, IC3-Modbus did not natively support reading 32-bit integer values directly.

Resolution

IC3-Modbus 4.05 and Later

Firmware version 4.05 introduced support for reading 32-bit values using Function Codes 03 (Read Holding Register) and 04 (Read Input Register).

Supported 32-bit data types:

  • Signed 32-bit
  • Signed 32-bit (swapped)
  • Unsigned 32-bit
  • Unsigned 32-bit (swapped)
  • Float 32-bit
  • Float 32-bit (swapped)

🔹 Note: This is a special case of the “2 register read” and requires two consecutive Sigma object numbers.

Refer to: Sigma - Release 4.06 - Firmware IC3-Modbus Release Note Section 11.4.2 – 32-bit Data Types


Other Sigma Versions (Pre-4.05)

To read a 32-bit integer from two 16-bit registers:

  1. Read both registers into separate Analogue Input (AI) objects.
  2. Combine the values using a programmable object:
    • Multiply the high register by 65536
    • Add the low register value

💡 Example Code Snippet

 
10 XFlo = POINT 0|64      ; High register
20 YFlo = POINT 0|65      ; Low register
30 ZFlo = (XFlo * 65536.0) + YFlo
40 RETURN VIA TEXT 200 VALUE ZFlo  ; Use a suitable text object

Notes

  • Ensure the register order (high vs. low) matches the device’s Modbus specification.
  • Use Text 200 or a similar object to display the final 32-bit value.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 8250
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore