Issue
How can logging configuration be removed from a controller in Sigma release 4.04?
Product Line
Satchwell BAS & SigmaEnvironment
Sigma Release 4.04
Cause
Sigma 4.04 does not provide a direct method to download an empty logging configuration file to a controller. This limitation requires a manual workaround to effectively remove logging configurations.
Resolution
There are two recommended methods to delete logging configurations from a controller:
Method 1: Manual File Deletion via Explorer
- Open Sigma and navigate to the Logging Configuration section.
- Delete the unwanted logging data set from the configuration.
- Using Windows Explorer, go to the controller’s folder location.
- Locate and delete the logging configuration file.
- Example filename:
T0025400.100T00254= Server00.100= Controller
- Example filename:
- In Sigma System Diagnostics, re-download the logging configuration to the controller to apply the changes.
Method 2: Minimal Logging Configuration
- In Sigma, go to Logging Configuration.
- Open the required log data set.
- Delete all objects in the data set except one.
- Set the remaining object to log very infrequently.
- Save and download the configuration as usual.
- Optionally, delete the log data set entirely.
- This will result in the controller logging only one object at a minimal rate.
- Upon the next download of controller files, logging will be effectively removed.