Sigma - Device Monitoring, Alarm Priorities, and Functionality

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Device Monitoring, Alarm Priorities, and Functionality
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1887 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Device Monitoring, Alarm Priorities, and Functionality

Picard Product_Support
‎2018-09-06 10:54 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-07 07:46 PM

Issue

Understanding the configuration and limitations of Device Monitoring alarms, including alarm priorities and functionality in Sigma systems.

Product Line

Satchwell BAS & Sigma

Environment

Sigma versions 4.04 and later.

Cause

Clarification is required on whether the Device Monitor alarm in Sigma can have its priority or functionality modified.

Resolution

Sigma 4.04 and Earlier

  • The Device Monitor alarm is fixed at priority level 29.
  • Alarm priority cannot be changed in these versions.

Sigma 4.05 and Later

  • A configuration file named deviceMonitor.xml is introduced.

  • This file contains parameters such as polling frequency, retry attempts, and alarm priority.

  • Example configuration snippet:

    <DeviceMonitor>
        PollFrequency="1001"
        NumberRetrys="3"
        AlarmPriority="29"
        MaxDelayResponse="5000"
        LogLongDelays="0"
    </DeviceMonitor>

    Note: Do not modify these settings without consulting support and fully understanding the implications.

  • Important: Any changes to deviceMonitor.xml require a Sigma server restart to take effect.


Functional Limitations

  • The Device Monitor alarm is not controller-based, which means:
    • It does not support routing like plant alarms.
    • It cannot have “actions” applied.
    • There is no object associated with each controller.
    • It cannot be displayed on graphics or used in control schemes.

Recommendation

If enhanced functionality is required, consider using the legacy method where controllers are monitored by other controllers. This approach allows for more flexible alarm handling and integration into control strategies.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (4)
  • Find more articles tagged with:
  • 11717
  • alarms
  • communications
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore