Guidance on configuring a Sigma Distributed Network Node (DNN) when connecting to a subnetted Ethernet network.
Satchwell BAS & Sigma
  • Satchwell Sigma
  • Subnetted Ethernet network
A subnetted Ethernet network consists of multiple subnets. For example:
  • Network: 10.158.1.0
  • Subnet Mask: 255.255.255.0
  • Valid IP range: 10.158.1.1 to 10.158.1.254
  • Another subnet might be: 10.158.2.0
In such environments, the Sigma DNN must be configured with:
  • A valid IP address
  • A Subnet Mask
  • A Static Route
  1. Assign IP Configuration
    • Set the DNN’s IP address and subnet mask according to the subnet it resides in.
  2. Configure Static Route
    • Use the Pocket Terminal 32 program.
    • Syntax:
      SR+ 0.0.0.0/0 <Default Gateway IP> <Ethernet Port Number>
    • Example:
      If the default gateway is 10.158.1.254 and the Ethernet port is 5, enter:
      SR+ 0.0.0.0/0 10.158.1.254 5
  3. Disable RIP (Routing Information Protocol)
    • RIP is enabled by default and may interfere with static routing.
    • To disable RIP on port 5:
      • Open Pocket Terminal
      • Enter:
        RIPD 5
      • Click Send
  4. Inform IT Network Administrators
    • Since RIP is disabled, sublan routes are not broadcast.
    • Ensure that manual routing entries are added to network routers.
Additional Notes
  • This configuration ensures reliable communication between Sigma controllers and the DNN across subnet boundaries.
  • Always verify routing with IT before deployment.