Issue
How to configure the new surface mount Analogue Output boards to provide a 0–20 mA control signal instead of the default 0–10 V output.
Product Line
Satchwell BAS & SigmaEnvironment
- Sigma UNCX96 Outstations
- New style surface mount Analogue Output boards
Cause
Some connected field devices require a 0–20 mA signal for proper operation. The new AO boards support both 0–10 V and 0–20 mA outputs but require manual configuration to switch between these modes.
Resolution
To configure the AO board for 0–20 mA output:
-
Identify Channels:
- Only Channels 15 and 16 on the new surface mount AO board support 0–20 mA output.
-
Locate Link LK1:
- On the AO board, find the LK1 jumper associated with each channel.
-
Set Output Mode:
- To enable 0–20 mA output, move the LK1 jumper to the 0–20 mA position.
- To revert to 0–10 V output, place the jumper back to the 0–10 V position.
⚠️ Important: Ensure power is turned off before adjusting the jumper settings to avoid damage or incorrect configuration.