Sigma – Analogue Input Channels Display Incorrect Values

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma – Analogue Input Channels Display Incorrect Values
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa125819
    sesa125819
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1174 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma – Analogue Input Channels Display Incorrect Values

Picard Product_Support
‎2018-09-06 12:39 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-21 06:25 PM

Issue

Analogue input (AI) channels are not displaying the correct values.

Product Line

Satchwell BAS & Sigma

Environment

Sigma Analogue Input

Cause

The issue is observed across multiple analogue input channels, cards, and controllers. This widespread behavior suggests the root cause is likely external to the individual AI objects or hardware components.

Resolution

Follow the steps below to isolate and resolve the issue:

Scenario 1: Issue Occurs on a Single Controller

  1. Isolate Inputs:

    • Disconnect all inputs to the AI card except one.
    • Use a known resistive input for testing.
  2. Test Input Stability:

    • Replace the connected analogue input with a fixed resistor.
    • Observe the reading—if it stabilizes, investigate the other inputs for faults.
  3. Verify Voltage Reading:

    • Change the object lookup table entry to 2000.
    • Measure the voltage across the resistor.
    • Compare the measured voltage with the maximum input voltage (2V).
      • Example: If measured voltage = 1.5V
        Calculation: 1.52.0=0.75×100=75\frac{1.5}{2.0} = 0.75 \times 100 = 752.01.5​=0.75×100=75
        The AI object should display 75.
  4. Check Earthing:

    • Ensure the controller’s earth bar is properly connected to a good earth.
  5. Hardware Checks:

    • If the issue persists, consider replacing the AI card.
    • If unresolved, consider replacing the CPU card.

Scenario 2: Issue Occurs on Multiple AI Cards in One Controller

  1. Repeat Isolation Steps:

    • Disconnect all AI inputs on all cards.
    • Connect only one resistive input to a single card and observe behavior.
  2. Repeat Steps 3–5 from Scenario 1.


Scenario 3: Issue Occurs Across Multiple Controllers

  1. Check Earthing:

    • Confirm all controller earth bars are securely connected to a good earth.
  2. Inspect Power Supply Boards:

    • Older power supply boards (especially in BAS-to-Sigma upgrades) may cause various issues.
    • Overheating of voltage regulator ICs due to loose securing bolts can lead to ‘current limit’ mode.
    • Action: Retighten bolts securing the regulator tabs and TO3-type regulators. Allow the heatsink to cool down.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 7368
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore