Issue
The Analogue Input (AI) Objects were functioning correctly but suddenly failed. Instead of displaying the expected default value of 20.0, they now show their last recorded value. Upon testing, the inputs return different values, and temperature detectors consistently read 150°C, while heat flow rates show 0 m³/hr.
Product Line
Satchwell BAS & SigmaEnvironment
Sigma UNCX96 Analogue Input (AI) card
Cause
The issue stems from incorrect controller slot allocation. The slot is mistakenly configured as empty, which prevents the AI card from functioning properly.
Resolution
To resolve the issue:
- Access the controller configuration.
- Verify the slot allocation.
- Ensure the slot is correctly assigned as an Analogue Input (AI).
- Download the updated configuration to the controller.