Sigma Alarms Not Received at the Enterprise Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Alarms Not Received at the Enterprise Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1567 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Alarms Not Received at the Enterprise Server

Picard Product_Support
‎2018-09-11 12:53 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 05:24 PM

Issue

Sigma controllers generate alarms, but these alarms are not received or displayed at the Enterprise Server during normal operation. However, when alarms are manually triggered from the Enterprise Server, they are received correctly.

Product Line

EcoStruxure Building Operation, Satchwell BAS & Sigma

Environment

  • Building Operation Enterprise Server
  • Satchwell Sigma

Cause

This behavior is typically caused by firewall restrictions:

  • When the Enterprise Server initiates communication with Sigma controllers, alarm messages are allowed through the firewall and displayed correctly.
  • When the Sigma controllers initiate communication (i.e., during normal operation), the firewall may block these inbound messages, resulting in delayed or missing alarms.

Resolution

To resolve this issue, allow inbound communication to the Enterprise Server on UDP port 49152.

Firewall Configuration Options:

  • If Windows Firewall is not used:
    Refer to your firewall vendor’s documentation for instructions.

  • If Windows Firewall is used but managed by IT:
    Contact your IT department to request the necessary exception.

  • If Windows Firewall is used and you have access:
    You can manually add the exception or use the unofficial tool SBO Firewall Config.

    Note: While not officially supported, this tool has been successfully used at various sites.

For manual configuration steps, refer to:
Using Sigma on Windows 7 with Firewall


⚠️ Important Notice

Sigma is not supported in EBO 2022 and later.
To continue supporting Sigma devices, you can implement a multi-version system:

  • Keep Enterprise Servers with Sigma devices on Building Operation 3.2.
  • Add a Building Operation 2022 or later Enterprise Central
  • Upgrade the rest of the system to Building Operation 2022 or later.

You will not be able to upgrade EcoStruxure Building Operation servers that contain unsupported protocols, objects, or devices. Attempting to do so will result in failed upgrades or loss of functionality.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
Tags (2)
  • Find more articles tagged with:
  • 18307
  • CraigEllis25
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore