Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Setting up a Local / Internal NTP Server to allow time synchronization

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting up a Local / Internal NTP Server to allow time synchronization
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Dave_Shore
    Dave_Shore
  • chris_clerc
    chris_clerc
  • CraigEl
    CraigEl
  • Chris_Asbury
    Chris_Asbury
  • sesa139513
    sesa139513
  • BillNeville
    BillNeville
  • Derrick_Ratliff
    Derrick_Ratliff
  • PaulFr
    PaulFr
  • LeeCravens
    LeeCravens

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
16472 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting up a Local / Internal NTP Server to allow time synchronization

Picard Product_Support
‎2018-09-11 01:37 PM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:45 AM

Issue

When external internet access is not possible an alternative NTP Server is required to allow ES and AS to by time synchronized onsite.

Product Line

EcoStruxure Building Operation

Environment

  • Enterprise Server / Automation Server on closed network

  • Eg Windows 7

Cause

AS will not synchronize the time with a local NTP such as Windows 7 (32 or 64 bit) without it first being configured.

Even then, increasing Cyber Security features within EBO means that the use of a 3rd Party NTP is becoming a much better option.

Resolution

Preferred Solution

The very best option for the latest versions of EBO would be to investigate. Meinberg NTP which is a third party NTP server that runs on the Win7 or Win10 OS and provides NTP by synchronizing with four or more Internet clocks and is a trusted time source in NTP.  It is not an officially supported PSS tool, but it does fix the issue of the ES/AS not trusting the time.  

Windows 7  Config

If you still wish to attempt the Windows 7 NTP option first the procedure to setup is as follows:   

  1. In the 'Services' window (part of Administrative Tools) Stop the 'Windows Time' service if already running. The 'Startup Type' could be set as Manual or Automatic depending on the user needs.
  2. In the Registry Editor following changes to be made under the Key
    • HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\W32Time:
    • ** Config -> AnnounceFlags = 5.
    • **
    • HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\W32Time\TimeProviders\NtpServer -> Enabled = 1.
  3. Start the 'Windows Time' service in the 'Services' window(part of Administrative Tools).
    Note: NTP uses UDP Port 123
    Below is a Wireshark capture using filter udp.port == 123 indicating the “Leap indicator” bits are 11, meaning “clock unsynchronized”.

NOTE: The NTP client in the AS may ignore the time sent by the NTP server if the root dispersion is greater than 'X' seconds (unknown at this time). See Automation Servers ignore time sync message sent from Windows NTP server that uses local internal cl... for information on how to determine whether this is a problem at the site and how to resolve it.

Note: Test Lab results show that once validated and synchronized, the AS asks the time from the NTP about every 17 minutes.

Two enhancements have been requested for a future release:

  1. Workstation gets an alarm if the NTP is not a valid reply
  2. A tick box setting in Workstation so the ES/AS can accept an invalidated reply(time)
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (6)
  • Find more articles tagged with:
  • 17178
  • alm
  • DavidShore20
  • PeterLarsen23
  • qc27050
  • qc794
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore