Setpoints and Commands from Niagara objects are not being written to the BACnet points
  • Setpoints and Commands from Niagara objects are not being written to the BACnet points
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
‎2018-09-06 09:59 AM
I/A Series R2 WorkPlace Pro and UNC
I/A Series MNB controllers
The BACnet objects are located in a PollOnDemand container. BACnet objects in the PollOnDemand container will only be polled when linked Gx objects (graphics) are viewed. In this particular case, these BACnet objects are not required to be displayed on graphic pages and thus they are not linked to any Gx objects.
being viewed
Create GxText objects in the PollOnDemand container and link the BACnet objects' outputs to the GxText objects. With this, the BACnet objects will be polled when the PollOnDemand container is viewed.
  • TAC IA Series
Tags (2)
  • 14589
  • update