Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Send unique SNVTs to more than 13 controllers or groups

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Send unique SNVTs to more than 13 controllers or groups
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1469 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Send unique SNVTs to more than 13 controllers or groups

Picard Product_Support
‎2018-09-07 01:20 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:04 PM

Issue

What if you need to send unique SNVTs to more than 13 controllers or groups from a Xenta base unit?

Product Line

TAC Vista

Environment

  • LNS System
  • LON Devices
  • LonMaker/NL220

Cause

All devices with Neuron chips in them use an address table. This table holds the neuron addresses or group addresses of each device or group that receives a SNVT from it. That table only holds 15 entries and 2 of them are used in the base units for the TAC group and the Xenta group leaving only 13.

Resolution

If the signals are sent to a group that only occupies one entry in the address table of the sender and one in each receiver. If the binding is unacknowledged, one entry is taken in the sender for each node or group but not in the receivers.

So what if you need a unique occupancy signal for 50 controllers? Or a unique temperature setpoint for them? A group binding will not do because that is one single value to the entire group.

The Loytec L-Proxy communicates on Lon networks and is commissioned like other Lonworks devices but uses a proprietary chip set instead of a neuron. This allows its address table to contain 384 entries. It can also have up to 5 ports which can all be commissioned in the same network.

So if you send all of your SNVTs from the base units to the L-Proxy (up to 125 of them from a 401), you can let the L-Proxy distribute them to the rest of the devices. Another benefit of that chipset is that the throughput is much greater than the neuron so it can handle such a load.

Related Articles:

  • Bind to more than 13 unique LON devices without running out of address table entries
  • No more address table slots for a device involved in the attempted connection. (Subsystem: NS Connec...
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 1800
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore