Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Security Expert Data Service fails to start with error 1067

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Security Expert Data Service fails to start with error 1067
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • AbeMeran
    AbeMeran
  • AdamSteele
    AdamSteele
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2984 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Security Expert Data Service fails to start with error 1067

Captain AbeMeran Captain
‎2021-10-26 11:16 AM

Last Updated: Kirk AdamSteele Kirk ‎2025-04-07 10:21 PM

Issue

Security Expert Data Service fails to start with error 1067: The process terminated unexpectedly 

DataServiceErr.PNG

Product Line

Security Expert

Environment

Security Expert Server

Cause

  • Port used by the service is blocked or already in use
  • Permission issues with the service logon account
  • Prerequisite .NET Framework is incomplete or not installed correctly

Resolution

  1. In Windows go to Windows Features and ensure that all .NET Framework items show a check mark to indicate that each sub item has been enabled. See Ensuring Windows features are installed for Security Expert SOAP service for details.
  2. In Windows Event Viewer, examine the Application log, it will typically have an entry with details about the reason for the error.2021-10-21_10-59-06.jpgIn this case, we see an Address Already In Use Exception in the Socket Connection Listener. This is a clue the error is with the network port. The Security Expert data service has been configured to use the default port 8000.
  3. On the server, list the network ports using netstat.2021-10-22_10-07-14.jpg
    We can see PID 5660 is already using the port.
  4. Get the name of service associated with PID 5660.2021-10-22_10-08-17.jpg
  5. Once the service is identified, take corrective steps to ensure the two services don't use the same port.
  6. Make sure the Windows account the service is using to log on has the appropriate permissions.
  7. If port 8000 isn't being used, first Reboot the Security Expert PC and if the error still persists, uninstall Security Expert, reboot and reinstall.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (8)
  • Find more articles tagged with:
  • 1067
  • AbeMeran21
  • AdamSteele25
  • AlanWood22
  • Data Service
  • process
  • terminated
  • unexpectedly
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of