STR 350/351 manually setup without plug-in (nciOption1 and nciOption2)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • STR 350/351 manually setup without plug-in (nciOption1 and nciOption2)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4586 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

STR 350/351 manually setup without plug-in (nciOption1 and nciOption2)

Picard Product_Support
‎2018-09-07 04:08 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 07:01 PM

Issue

If the STR 350 plug-in is missing, then the STR 350/351 setup needs to be performed manually in NL220, LonMaker, TAC Vista Workstation, or TAC Menta.

Product Line

TAC Vista

Environment

  • TAC Vista 5.1.4, TAC Vista 5.1.5
  • Windows 7, Server 2008

Cause

Not all plug-ins in the TAC ToolPack can run on Windows 7 or Windows 2008.

Read details in TAC ToolPack plug-ins are not showing up.

Resolution

If the STR 350 plug-in is missing, then the STR 350/351 setup needs to be performed manually in NL220, LonMaker, TAC Vista Workstation, or TAC Menta.

NL220 STR 350/351 setup steps are shown below:

  1. Use the STR 350 device template to create a new node on the channel.
    Note: the device template is located at C:\LonWorks\import\TAC\IO Modules (Default location)
  2. Double click on the STR 350/351 device and make necessary changes to any signal under “NVs” tab.

TAC Workstation STR 350/351 setup steps are shown below:

  1. Expand the tree structure in the left panel.
  2. Select the desired signal to change in the right panel.

If a STR 350/351 is connected to a programmable controller (Xenta 280/300/400), then the STR 350/351 can be added in the Menta file similar to an IO module. Setup steps are shown below:

  1. Under “Options/Device Specification” select “Add STR Module…"
  2. Under “Type” Select “STR350/351” and Under “Bit(s)”, choose the desired bit(s).
    Note: hover over each bit, there is a short description about the selected bit.

If a STR 350/351 is connected to a Xenta Server (Xenta 7XX), then the STR 350/351 can be added in the Xbuilder project similar to an IO module. Setup steps are shown below:

  1. In Network panel,  under “LON", right click and select “Add IO Module->STR35X".
  2. Right click on the STR35X model just added, and select "Configure".
  3. A configuration pop up window will be displayed.  Make any desired changes.
    Note: Neuron ID can be manually typed in the Xbuilder or get from service pin in the Workstation. If choose to service pin, need to create and commission a LNS network in Workstation.
  4. Save and download the project.

Below is a table of each bit in nciOption1 and nciOption2 and its brief description.

nciOption1:

Bit 0, 1: Fan type 00: No fan (Default)
10: On/Off fan
01: 2 speed fan
11: 3 speed fan
Bit 2: Fan auto state 0: Not allowed (Default)
1: Allowed
Bit 3: Fan off state 0: Not allowed (Default)
1: Allowed
Bit 4: Fan speed 1 0: Not allowed (Default)
1: Allowed (On/Off fan type needs to be activated)
Bit 5: Fan speed 2 0: Not allowed (Default)
1: Allowed (2 speed fan type needs to be activated)
Bit 6: Fan speed 3 0: Not allowed (Default)
1: Allowed (3 speed fan type needs to be activated)
Bit 7, 8 ,9: Not used  
Bit 10: Temperature presentation 0: °C (Default)
1: °F
Bit 11: Temp. normally displayed 0: Setpoint temperature (Default)
1: Room temperature
Bit 12: Setpoint temp. presentation 0: Absolute temperature (Default)
1: Offset temperature
Bit 13: Bypass button usage 0: Bypass (Default)
1: On/Off
Bit 14: Not used  
Bit 15: Supported protocols 0: Standard LonTalk protocol only
1: Standard LonTalk protocol and TAC proprietary protocol (Default)

nciOption2:

Bit 0, 1: Sunblind - Switch 1 00: On/Off (Default)
10: Up/Down
01: On/Off/Up/Down
11: Not used
Bit 2, 3: Sunblind - Switch 2 00: On/Off (Default)
10: Up/Down
01: On/Off/Up/Down
11: Not used
Bit 4: Light - Switch 1 0: Disable (Default)
1: Enable
Bit 5: Light - Switch 2 0: Disable (Default)
1: Enable
Bit 6, 7, 8: Local sensor 000: None (Default)
100: CO2
010: RH
001: Occupancy
Bit 9: CO2/RH value 0: Hidden (Default)
1: Display
Bit 10-15: Not used  
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4346
  • thermostat
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore