SSL and Modbus functions
  • SSL and Modbus functions
  • CraigEl
    CraigEl
  • SaidSawan
    SaidSawan
‎2018-09-11 12:48 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 10:42 PM
Modbus device in hand does not have a pre-configured widget in the device list of Building Expert. A script is required to communicate with the device
EcoStruxure Building Expert
  • SmartStruxure Lite Multi-Purpose Manager
  • Any modbus device
Pre-configured widget not available in the device list of Building Expert
The MPM can only be a Modbus Master; meaning it can request information from other slave modbus devices, or write to them.
Terminals A and B on the MPM correspond to modbus terminals (Serial +) and (Serial -) respectively.
When using a script to communicate with modbus devices, the "Enable" box in the ModBus configuration object (MOD1) must be disabled to allow the MPM to communicate with the devices using a script.
The modbus port should then be closed (in case it was left open) and re-opened using the following functions
@@@ Lua.modbus.close       (Description and example here)
@@@ Lua.modbus.open        (Description and example here)
The following are the standard modbus functions and their corresponding Lua functions used in the MPM
Modbus Function Code Lua Function in MPM
Function Code 01 modbus.coil_read
Function Code 02 modbus.di_read
Function Code 03 modbus.hr_read (16-bit)
Function Code 04 modbus.in_read
Function Code 05 N/A
Function Code 15 modbus.coil_write
Function Code 06 modbus.hr_write
The following are the 8 different modbus functions that can be used to read/write to registers from/to modbus devices
@@@ Lua.modbus.coil_read     (Description and example here)
This function is equivalent to : [Function Code 01 (01 HEX)]
@@@ Lua.modbus.coil_write    (Description and example here)
This function is equivalent to : [Function Code 15 (0F HEX)]
@@@ Lua.modbus.di_read      (Description and example here)
This function is equivalent to : [Function Code 02 (02 HEX)]
@@@ Lua.modbus.hr_read       (Description and example here)
This function is equivalent to : [Function Code 03 (03 HEX)]
@@@ Lua.modbus.hr_write      (Description and example here)
This function is equivalent to : [Function Code 06 (06 HEX)]
@@@ Lua.modbus.in_read      (Description and example here)
This function is equivalent to : [Function Code 04 (04 HEX)]
@@@ Lua.modbus.fp_read     (Description and example here)
@@@ Lua.modbus.fp_write    (Description and example here)
To read a floating-point (32-bit) value, the fp_read() function can be used. (Download script)
To read an unsigned long (32-bit) value the hr_read() function can be used, however, some data manipulation is required (Download script)
To read a floating-point (64-bit) value, the hr_read() function can be used. (Download script)
Modbus errors can be found here
  • EcoStruxure Building Expert
  • 17871
100% helpful (1/1)