Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SE8000 does not retain settings after power loss

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SE8000 does not retain settings after power loss
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • SaidSawan
    SaidSawan
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6116 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SE8000 does not retain settings after power loss

Product_Support
‎2018-09-10 10:43 AM

Last Updated: CraigEl Champion ‎2022-08-08 06:22 PM

Issue

Power cycling the SE8000 room controller will cause the settings to revert to default. This requires reconfiguring each of the parameters once again.

Product Line

EcoStruxure Building Expert

Environment

  • Multi Purpose Manager
  • Automation Server
  • SE8xxx Room controller
  • SE8000 Series
  • SER8300, SE8300, SE8350
  • Ex. Viconics branding VT8000 Series

Cause

This has to do with BACnet priority; if the configuration was not written with the appropriate priority, the Room controller will overwrite the parameters upon a power cycle and set them to default.

Resolution

There are a few ways to prevent the SE8000 from reverting to its default settings after a power cycle:

  1. Configuring each Room Controller locally by navigating to the configuration menu. (Centralized and Standalone system)
  2. Using a LUA4RC script (Centralized and Standalone system)
  3. Writing to points with a specific priority via the BACnet front-end (Centralized system)

NOTE: Since Zigbee does not have any command prioritization mechanisms, setting the parameters from an MPM via Zigbee will not be retained after a power cycle and is strongly not recommended.

All three methods can be used to configure a Room Controller prior to or after its installation. Configuration prior to installation can save a lot of time for the technician on site.  

 

1 - Configuration on SE8000 (Local)

  • Changing the parameters on the SE8000 locally will permanently save the settings and will also allow the user to change the parameters settings locally (e.g. Occupied cooling setpoint). This however can be time consuming.

 

2 - Configuration via LUA4RC

This method is especially useful in standalone applications with no BACnet front end. If there are many parameters that need to be adjusted, it will be quicker to upload the script to each of the Room controllers rather than navigate to each parameter manually.

  • By default, when you assign a value to a BACnet point, the write priority will be priority 16
    Example:
    ME.MV6 = 2 --Set "Network Units" to Imperial (blocked by using priority 16, not user-adjustable)
  • To write to another priority, an array is used
    Example:
    ME.MV4_PV[3] = 1            --Language will be blocked by user, room controller and bacnet front-end. Will be saved to memory and will stay after a power cycle

NOTE: To release this priority, you can set it to nil (example: ME.AV25_PV[8] = nil).

  • To access the relinquish default, priority 17 can be used
    Example:
    ME.MV10_PV[17] = 1    --Set "Occupancy Command" to "Local Occupancy"; here it is mandatory to have (_PV[17]) because thermostat must be able to toggle between "Occupied" and "Unoccupied" temperature
  • Use the script below as a template for your LUA4RC script (remove comments to use less memory)
    if not init then
    
      ME.MV6 = 2           --"Network Units"
      ME.MV10_PV[17] = 1   --"Occupancy Command" 
      ME.AV46_PV[17] = 3   --"Standby Temperature Differential"
      ME.MV5 = 2           -- "Time Format"
      ME.AV67_PV[17] = 4   --Standby Time
      ME.AV68_PV[17] = 12  --Unoccupied Time
      ME.MV46_PV[17] = 3   --UI 16 Configuration
      ME.MV4_PV[3] = 1     --Language
                           --Add all required configuration parameters
    init = true
    end

 

3 - Configuration Via BACnet:

SE8000 parameters can be configured via the BACnet front end by using the following priorities:

  • Priority 2 or 3: Using these priorities will permanently save the setting on the SE8000 and will not allow the user to change the settings locally.
  • Relinquish default: This will allow the user to change the value locally on the SE8000. This is typically used with setpoints

NOTE: using Priority 16 will not allow the user to change the value locally on the SE8000, however, the SE8000 will revert to value to default upon a power cycle.

Another effective method is to push the configuration to multiple SE8000s across the network using a lua script. See Bulk Lua4RC upload via BACnet (Mass upload).

Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (3)
  • Find more articles tagged with:
  • 18946
  • se8600
  • se8650
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore