SE7000/SE8000 Room Controller status shows an "offline (-2)" error.
  • SE7000/SE8000 Room Controller status shows an "offline (-2)" error.
  • Ramaaly
    Ramaaly
  • SaidSawan
    SaidSawan
‎2018-09-06 09:30 AM
Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2022-04-05 08:19 AM
Room controller shows up in the Discovery (Bind) window but will not go online after clicking on “Bind device”. Status in the ZVC object shows “offline (-2)” error.
EcoStruxure Building Operation, EcoStruxure Building Expert
  • Building Operation Workstation
  • Building Operation Automation Server
  • SSL SE8000
  • SSL SE7000
An invalid value is being overwritten continuously to a local point (to the Room Controller) by a dashboard widget or a third-party device(e.g. via Bacnet).
The invalid value must be corrected before proceeding with the binding process.
Example: A value of 0 is being written to the Occupancy command point which only take values of ([1 = Local Occupancy], [2 = Occupied] or [3 = Unoccupied]). The write and read traffic generated prevents other room controllers from joining the network.