S4 Open Appliances Quick Start Guide Metasys: N2 Integration to SBO

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • S4 Open Appliances Quick Start Guide Metasys: N2 Integration to SBO
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Cody_Failinger
    Cody_Failinger
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3726 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

S4 Open Appliances Quick Start Guide Metasys: N2 Integration to SBO

Picard Product_Support
‎2018-09-10 02:06 PM

Last Updated: Picard RobertAndriolo Picard ‎2022-10-20 06:09 PM

Issue

Metasys® N2 Integration to SBO

Product Line

EcoStruxure Building Operation

Environment

  • Struxureware Building Operation
  • Metasys N2

Cause

This Quick Start Guide will assist the Schneider Electric branch or dealer installation team with the basic steps to bring the virtual BACnet devices emulated by the S4 Open: BACnet-N2 Router into the SmartStruxure environment as part of a Johnson Controls Metasys® N2 integration into SBO.

This document is not intended to be a full tutorial or user manual for either the S4 Open: BACnet N2 Router or the SmartStruxure system. Refer to the manufacturer’s documentation for each of these systems for detailed information. S4 documentation, the complete Device Template library, and support utilities can be found on the support CD delivered with your S4 Open appliance.

Please contact the S4 group for any questions on this process. 

Resolution


Step 1:
 
  1. Follow the installation instructions provided with the S4 Open: BACnet-N2 Router to discover and publish the N2 devices in the Metasys® installation to BACnet IP. All operations in SmartStruxure will be against these emulated BACnet IP devices each representing the underlying N2 device.
    S4ManagementConsole.png
  2. Investigate before you integrate! Validate the N2 bus to make sure that it is electrically in spec and that all N2 devices are working properly before starting the integration process.
  3. Assign a unique BACnet virtual network number to each S4 Open: BACnet-N2 Router. N2 devices connected to this S4 Open appliance are published as emulated BACnet IP devices under that network.
  4. The Configure Wizard in the S4 Open Management Console will assist you with generating a unique BACnet Device ID for each N2 device. Point instance numbers are included as attributes in our Device Templates for all application-specific controllers. Either of these can be manually overridden in the S4 Open Management Console to meet unique requirements.
  5. The S4 Metasys® Configuration File Conversion Utility can be downloaded from the S4 Group web site and will assist you in creating custom Device Templates for DX-9100 devices or application-specific controllers. You will need the corresponding .DMO or .PRN files as input to this utility.
  6. A detailed understanding of Metasys® N2 devices, the Metasys® system, and the associated configuration and commissioning utilities are necessary to support successful integrations. If you don’t have this expertise in-house, The S4 Group can recommend a consultant to assist you.

NOTE: We highly recommend that you attend a two-day S4 Boot Camp to make sure that you have all the skills necessary to install and configure the S4 Open: BACnet-N2 Router.

Step 2:
  1. Bring up the SmartStruxure BACnet discovery tab and select BACnet devices. In this example, you can see that the S4 Open BACnet-N2 Router was defined in Network 1 and the N2 devices are in Network 122. The other device in Network 1 in this example is a JCI NAE.
    ServerDiscovery.png
  2. The best practice is to assign the S4 Open: BACnet-N2 Router to the BACnet network that you are using as your BACnet backbone. As with any BACnet device, the BACnet-N2 Router must be assigned a unique BACnet device ID.
Step 3:
  1. Expand the navigation pane to expose the BACnet Interface / IP Network folder. Then select and drag the N2 devices from the Device Discovery tab to the IP Network folder. SmartStruxure will tell you that an Upload is required. Respond OK.
    DeviceDiscoveryUpload.png

Step 4:
  1. Navigate to the IP Network folder, select the properties page for each device, and request an Upload operation. This will bring the device properties and point list for each N2 device into SmartStruxure.
    DeviceProperties.png
  2. SmartStruxure will respond with the following confirmation as each upload is completed.
    ProgressView.png
Step 5:
  1. When the Upload process is completed for all N2 devices and the S4 Open: BACnet-N2 Router, you can continue your SmartStruxure installation process as you would for any BACnet device.
    ApplicationFolder.png
  2. Note that there will be no points published under the S4 Open: BACnet-N2 Router itself but you will be able to confirm the Operational Status of the system from SmartStruxure.
    ApplicationFolder2.png

The Schneider Electric support organization will supply pre-sales engineering support and first-level technical support for the Metasys® N2 to SBO integration solution. The S4 Group will be available to provide 2nd level support to these integration projects.

 
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 18669
  • RobertAndriolo20
  • RobertAndriolo22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore