Return Authorization Number for a defective Niagara R2 UNC

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Return Authorization Number for a defective Niagara R2 UNC
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • WaynePeters
    WaynePeters
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1852 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Return Authorization Number for a defective Niagara R2 UNC

Picard Product_Support
‎2018-09-07 01:57 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:27 PM

Issue

Steps in obtaining a Return Authorization (RA) number for a defective Niagara R2 UNC.

Product Line

TAC IA Series

Environment

Niagara R2 UNC

Cause

Failed unit requires repair or replacement.

Resolution

Before calling Customer Service for a Return Authorization, review the following steps to ensure the unit needs to be sent back to the factory.

Symptom: Unit has a constant / steady heartbeat LED

A UNC with a steady heartbeat LED indicates that the unit is not booting to the operating system. If a power cycle does not correct, there is not a way to recover without repairing with the factory fixtures. The only alternative is to provide a return authorization for repair or replacement. UPDATE: There are some issues that have been identified since this article was originally published that are field repairable.  To identify these field repairable issues, connect the serial console (see Need to correct invalid IP address or subnet mask entered into a UNC 520), power cycle the UNC and capture the console output.  Provide the console output information when you contact Product Support.

Symptom:  Unit has a rapid heartbeat

A rapid heartbeat typically indicates a memory issue.  During shipping the memory card has been known to have shifted in its socket. Power the unit down and remove then reseat the memory card in the UNC several times and then power up and monitor.

Symptom: Unit is continuously rebooting

In a new unit, this continuous rebooting could be a memory issue.  During shipping the memory card has been known to have shifted in its socket. Power the unit down and reseat the memory card in the UNC several times and then power up and monitor.

Typically, if the fuse is bad you would see a watchdog or battery failure in the standard output window every 15 minutes or so. The fuse in the UNC-410 and UNC-520 is soldered into the board and is not field replaceable. The UNC-510 fuses are field replaceable.  Remove the shield from the UNC enclosure and remove the board from the shield. The main fuse (F1) is a 5 X 20 mm Fast Acting 1.5 amp 250 volt (Bussman GMA-1.5). The battery fuse is a 5 X 20 mm Slow Blow 2.0 amp 250 volt (Bussman GMD-2A). The battery fuse is the fuse on the right when the power connector is oriented to the upper right. Both fuses are labeled on the circuit board legend.

The control board tests the battery’s charge every 5 minutes by placing a momentary short across the battery and monitoring its recovery. A failing battery will cause the unit to reset and reboot when self- tested. Remove the battery red wire and if the unit continues to operate, replace the battery. To test the battery, disconnect the battery and measure the voltage across its terminals with a voltmeter. It should read above 12 Vdc. The charging circuit in all UNCs usually provides a voltage of 13.5 Vdc (approximately).
 
Replacement battery, part number UNC-500-BAT.

Notes: UNC will power itself down within 5 minutes after the power fails.

  • The battery will retain the clock and other dynamic memory data for about 12 hours.
  • A fully discharged battery will recharge in about 12 hours.
  • The life of a battery is 3 to 5 years under normal conditions.
  • Excessive discharge cycles or operation at high ambient temperature (>122F) will shorten the life of the battery.

UPDATE: There are some additional issues that have been identified since this article was originally published can cause the UNC to continuously execute a Watchdog Reset and become disabled. See I/A Series R2 (Niagara) station opened in the Admin Tool displays "Disabled"), for more information on this issue.

Symptom: AC power failure or Transformer problem

The UNC-410 and UNC-520 have an internal transformer. The transformer voltage and wiring should be verified before returning the unit.. This is a center-tap transformer and is wired to the first three terminals on the circuit board connector.  The wires, top to bottom, should be Green, Green Yellow, and Green respectively. The voltage should read approximately 30 VAC Green to Green and approximately half the value (15 VAC) between either Green wire to the Green Yellow wire.

Returning unit for repair

The symptoms above are a sample of common, sometimes field repairable, failures in a UNC. If the UNC-410 or UNC-520 needs to be sent to the factory for repair, you will only need to return the circuit board (UNC-410-500 or UNC-520-500), not the entire UNC. The printed circuit assembly will be exchanged or repaired and returned. The repaired UNC will come with a 3 month warranty.

To issue a Return Authorization (RA#) the factory will need to know the following information:

  • The product part number
  • Is the unit still under warranty? Warranty note: Warranty on a new UNC is 2 years from date of manufacture. The date code format is yyww. Example:  0815 is  2008 week 15
  • Serial number
  • Job name (site name for unit)
  • Factory order number
  • Project ID
  • Host ID (in the license file)
  • The reason for return
  • Network settings (IP, Subnet, name)
  • Username and Password
  • Station DB Username and Password
  • Any special shipping instructions
  • Have a purchase order number ready when you call. Note: Customer Support Services sends/bills for advance warranty replacement units. When the customer returns the correct unit within 30 days, a credit is then issued.,

Call Schneider-Electric at 888-444-1311 and select option 2 (Product Support). Product Support will enter a support case identifying the unit and that an attempt to troubleshoot was done prior to issuing the RA number. The caller should request the Product Support Case number and RA number for future reference.

An RA will be issued based on the following criteria:

  • Credit AWR (Advance Warranty Replacement). Customer is sending back an inoperable unit to the factory for credit and needs a replacement unit right away.
  • OOWR&R (Out of Warranty Repair and Return). Customer sends back an inoperable unit to the factory for repair and return.
  • IWR&R (In Warranty Repair and Return). Customer sends back an inoperable unit to the factory for repair and return.

NOTE: When issuing an AWR, hold the defective unit and use the packaging from the replacement to return the UNC board. This will help guarantee that the units are not damaged during shipment. When the units are received damaged and improperly packed, they are returned as received and no credit issued.

Ship the device to:

Schneider Electric
1354 Clifford Ave.   Dock 3
Loves Park, IL. 61111
Attn: Repair Dept. RA ######

Put the RA # on the outside of the box.
Include your return address in the box.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3369
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore