Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Need to correct invalid IP address or subnet mask entered into a UNC 520

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Need to correct invalid IP address or subnet mask entered into a UNC 520
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2092 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Need to correct invalid IP address or subnet mask entered into a UNC 520

Picard Product_Support
‎2018-09-06 01:35 PM

Issue

During initial setup, the incorrect ethernet IP address or subnet mask was entered.  Now when rebooting the UNC, I cannot reconnect to it using the I/A Series R2 Admin Tool.  How can the incorrect information be changed?

Environment

UNC-520 or UNC-410

Cause

Network connectivity cannot be established if the IP address or subnet mask was entered incorrectly.  Likewise, if an invalid subnet mask is entered, the UNC may not boot completely (or at all).

Resolution

The following information is provided in more detail in the section "Determining Network Settings", subsection "JACE-4/5" of chapter 3 of the Niagara Networking & Connectivity Guide.  This document is provided with and installed with the I/A Series (Niagara) R2 software.

Required hardware:

  • Serial Cable
  • Terminal Emulator software on computer (such as "Hyperterminal" or "Putty")

Procedure:

  1. Configure the Terminal Emulator to run at 9600 baud, 8 bits, one stop bit, no parity, hardware flow control
  2. Jumper the upper two pins of the Console "MODE" connector,  located in the upper right corner of the UNC-520 circuit board (See photo at right).
  3. Connect the terminal emulator via a UNCC-405 serial cable to port COM1 on the UNC and power-cycle the UNC.
  4. Wait for the UNC to complete its bootup process (do not break out of the boot process).
  5. Check the displayed information to determine what IP address and subnet mask was entered.

Power cycle the UNC and when the console display shows "Press any key to stop auto-boot"., press the space bar.

Follow the procedure in the section "Determining Network Settings", subsection "JACE-4/5" of Chapter 3 of the Niagara Networking and Connectivity Guide for the procedure to step through the settings changing them if necessary.  Please note that the figure 3-8 may not include all lines of information shown for your UNC.

If the serial console is showing any errors after you have verified the IP address / Subnet mask entries, please provide product support with a text copy of the serial console output showing the error messages.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5729
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore